Originally Posted By: KJay

I don’t see any Tamper Resistant 15A and 20A/125V single receptacles yet though, which I will assume be necessary for cord and plug connected dishwashers, over the range microwaves, etc.




I don't think these are on the required list.




How would you read 210.52-C(5)? this refers you back to C-1.

But the last sentence,".. or appliances occupying dedicated space shall not be considerd as these required outlets."

That I read as, rec in cabinets and other such areas and gas range rec etc. would not need TR rec.