If you have a grounding electrode at the generator this is a compliant SDS. Going to the 4 wire feeder is legal from that point. If you also have a grounding electrode in the disconnect enclosure at the building that makes the whole deal compliant. That can be the same electrode system if these are all grouped together.

IMHO


Greg Fretwell