Re: 240V only in a home and NEC? gfretwell Yesterday at 05:44 PM
I other than dwelling units your 6-15 would need GFCI protection in a kitchen.

Quote
(B) Other Than Dwelling Units. All single-phase receptacles
rated 150 volts to ground or less, 50 amperes or less and three-
phase receptacles rated 150 volts to ground or less,
100 amperes or less installed in the following locations shall
have ground-fault circuit-interrupter protection for personnel
14 1,707 Read More